I have a home network setup (modem, router, nuc) that draws around 50watts. While I understand a UPS is usually used to provide time for a gracefull shutdown, I am more interested in how long a UPS can provide power to my home setup in the event of an extended power outage.

I’m browsing various UPS brands and they commonly list available VA and W. How do I determine which of these models has larger battery capacity to keep my devices up for longer? Is it simply, the larger VA and larger W number, the larger the battery capacity? Since i’m not running many concurrent devices, I want to measure total duration under light load.

Given my system pulls around 50watts, whats the best way for me to determine how long a UPS can run given the specs listed on the product page? Do I need other variables to calculate runtime? Such as Power Factor? I can’t seem to easily find watt-hour battery capacity for most UPS.

I don’t want to purchase a large 3000VA, 2700W UPS if it doesnt actually have a longer runtime than say a 1500VA, 1500W UPS. How do I compare the two?

Answer from eslite on community.spiceworks.com
🌐
Reddit
reddit.com › r/homeserver › ups with long runtimes
r/HomeServer on Reddit: UPS with long runtimes
April 7, 2021 -

I see a lot of UPSes, but for typical use with a server, I'm only seeing about a half-hour of runtime on it.
Basically, I have enough for me to run around the house and safely shut everything down with some degree of cushion. I'd prefer something that I'd feel comfortable running for a while without power. We occasionally get power that goes down for a half hour to an hour. Are there any affordable UPSes (read less than $500) that can run for 4-6 hours on a similar load?

Ideally, I'd be looking for a 110V UPS that can use (possibly multiple) automotive/marine type batteries.

When you start to get into the thousands of dollars, a whole-home generator with automatic switch (and a small UPS to filter/deal with voltage fluctuations) starts to make more sense than a giant UPS.

🌐
NYTimes
nytimes.com › electronics › batteries and charging › the best uninterruptible power supply (ups)
The 3 Best Uninterruptible Power Supplies (UPS) of 2026 | Reviews by Wirecutter
September 17, 2025 - With six outlets on battery backup and 12 in total, this UPS can keep a Wi-Fi network running for up to three hours, or it can power your home-office setup long enough for you to save your work and shut down. ... This UPS offers the highest output and run time of any model we tested.
Discussions

How do I find which UPS has the longest runtime capacity for home use?
I have a home network setup (modem, router, nuc) that draws around 50watts. While I understand a UPS is usually used to provide time for a gracefull shutdown, I am more interested in how long a UPS can provide power to my home setup in the event of an extended power outage. More on community.spiceworks.com
🌐 community.spiceworks.com
7
7
October 17, 2023
Long Lasting UPS for Desktop
I am looking for a UPS that can backup my desktop (power consumption roughly 250W) for a long period of time (at least 2 hours, the longer the better) so far the best suitable option i found on the website is a 1500VA back-UPS with external battery pack, but even that is not enough to support ... More on community.se.com
🌐 community.se.com
4
0
June 29, 2021
UPS / Battery selection for "extreme" runtime (5-6 hours) for low power (<100W)?
This has become a recurring issue… In the telecom world, there are often situations where long runtime (1, 2, 5, or even 10 or more hours) would be required or ideal. In many cases this is a safety issue as phones can be a lifeline in industrial environments. More on community.spiceworks.com
🌐 community.spiceworks.com
11
4
August 26, 2018
UPS recomendation for Low power long run time
There has been a thread recently about swapping out Batteries in UPSs to extend runtime (eg: swapping 7Ah ones with 14 Ah ones to double run time). Manufacturers tend to say don’t consider this, get a UPS with a external battery packs & extend the run time that way. which is fine, but devices ... More on community.spiceworks.com
🌐 community.spiceworks.com
15
9
September 12, 2023
🌐
Eaton
eaton.com › au › en-gb › products › backup-power-ups-surge-it-power-distribution › backup-power-ups › long-runtime-ups.html
Long Runtime UPS - Uninterruptible Power Supply | Eaton
Eaton can help with a range of long runtime UPS systems for your needs. We’re a leading supplier of Back-up Power UPS, Surge, and Data Center Solutions that customers look to with complete confidence. Our technology ensures extended battery runtimes during power outages, providing resilience so you can operate as required without concern.
🌐
Family Handyman
familyhandyman.com › home › products
How Long Will an Uninterruptible Power Supply Last? We Tested 3 of Them
May 18, 2023 - When they were fully charged, I ... until the battery died and disconnected from the internet. CyberPower lasted the longest at five hours and 30 minutes, though APC was close behind....
🌐
Schneider Electric Community
community.se.com › schneider electric community › apc ups, critical power, cooling and racks › apc ups for home and office forum › long lasting ups for desktop
Solved: Long Lasting UPS for Desktop - Schneider Electric Community
June 29, 2021 - Share it with a Colleague! ... Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-21 05:48 AM ... Link copied. Please paste this link to share this article on your social media post. Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-21 05:48 AM · I am looking for a UPS that can backup my desktop (power consumption roughly 250W) for a long period of time (at least 2 hours, the longer the better) so far the best suitable option i found on the website is a 1500VA back-UPS with external battery pack, but even that is not enough to support 250W load for 120+ min.
🌐
CyberPower
cyberpowersystems.com › feature focus › higher capacity ups for longer runtimes
Higher Capacity UPS for Longer Runtimes | CyberPower
December 2, 2016 - Estimating expected UPS runtimes can be challenging, particularly when the consistency of the utility power is not well known. Selecting a UPS with a load capacity 30-35% above the required power load offers the advantage of longer runtimes.
Call   +18772976937
Address   4241 12th Ave E STE 400, 55379, Shakopee
Find elsewhere
🌐
Ecopowersupplies
ecopowersupplies.com › extended-runtime-ups
Eco Power Supplies
February 26, 2015 - Sorry for any inconvenience as we are no-longer taking online orders – please contact us directly by email, phone or via our enquiry page for our market leading range of UPS systems and accessories
Top answer
1 of 11
4

This has become a recurring issue… In the telecom world, there are often situations where long runtime (1, 2, 5, or even 10 or more hours) would be required or ideal. In many cases this is a safety issue as phones can be a lifeline in industrial environments.

When you run a typical sizing enquiry, many tools - like APC for example) will recommend a 1000VA UPS, and will claim that it should provide 500+ minutes for a 100Watt load (the load might be less than this - a POE switch for a half dozen phones could be as little as 60 watts).

Unfortunately in practice the UPS often shuts down exhausted after an hour or so.

One of my thoughts was to consider replacing the standard lead acid batteries with something better suited for long / deep discharge… as long as the charge current handling characteristics would be similar to a lead acid battery this might work?

Does anyone have any specific experience or recommendations?

Generators are NOT an option - in some cases these systems are in industrial environments - even if they are in office environments, the idea of running a generator for 100W of power is totally impractical. Central generation is not possible as there normally is no practical way to isolate / dedicate the power to the POE switches which are often distributed to locations close to the phones.

Any ideas / suggestions / discussion / experience welcome.

Thanks for your time!

Mitch

2 of 11
0

For my home server (mostly file server, some services) I’ve been using a Cyber Power PR1500LCD UPS, I can confirm that at 120watt load it will run for a little more than 3 hours, which surprised me because like you I’ve become accustomed to vastly under performing UPS systems from folks like APC (used to be my go-to brand honestly).

They have larger models as well, up to 3K I know so I believe you’d be able to get 6 hours or more at 100watts load, I’d recommend checking out their higher end UPS systems.

I’ve tagged Naomi and Craig from Cyber Power, I know both are active here and helpful, I’m sure they can help you find the right system for your needs.

@naomi-cyberpower @craig-cyberpower

🌐
Spiceworks
community.spiceworks.com › hardware & infrastructure
UPS recomendation for Low power long run time - Hardware & Infrastructure - Spiceworks Community
September 12, 2023 - There has been a thread recently about swapping out Batteries in UPSs to extend runtime (eg: swapping 7Ah ones with 14 Ah ones to double run time). Manufacturers tend to say don’t consider this, get a UPS with a external battery packs & extend the run time that way. which is fine, but devices that can do this tend to be the much higher capacity ones (ie 750Va +). I’ve got a scenario (similar to UPS / Battery selection for "extreme" runtime (5-6 hours) for low power (
🌐
Quora
quora.com › What-is-the-maximum-time-duration-a-UPS-uninterruptible-power-supply-can-operate-for
What is the maximum time duration a UPS (uninterruptible power supply) can operate for? - Quora
80% of power outages last under a minute, 90% last less than 5 minutes. 90% of outages lasting more than 5 minutes will last longer than 4 hours. Thus, there’s a financial breakpoint right around 5 minutes.
🌐
Reddit
reddit.com › r/homelab › long-running battery backup options?
r/homelab on Reddit: Long-running battery backup options?
August 8, 2021 -

I am in need of a UPS solution that doesn’t quite fit the typical scenario of desktop/rack battery backups…

Rather than keeping a full 200+ W computer on for a couple minutes while a generator comes on or the computer shuts down, I need to keep a router alive for up to 24 hours.

This is part of a fire safety requirement. The fire alarm is wired to use the internet service line; there is no phone line to the building. The fire alarm itself has a battery that is spec’ed to last for 24 hours, but we need to keep the router and fiber box alive for that time as well.

The router is a SonicWall TZ470, and although it will have a switch attached, the alarm will be directly connected and will be the only other device that remains powered in the case of an outage, so the load will be very low. I’m not sure what the fiber box is, but it’s got a 5W power supply.

After a few weeks of measurement, it seems the router and fiber box together use about 275Wh per 24 hours, with minimal contractor network traffic (so likely lower in an actual power outage).

Everything I can find online about traditional UPS systems show runtimes in the 10s of minutes and ratings in the hundreds of watts. I really only need like 30W rating, but enough capacity to last 24h. When I enter that into APC’s system builder, it recommends a $3000 multi-unit system, which is way overkill. It seems that these systems, while they can provide high instantaneous loads, cannot sustain a trickle for very long, or the data sheets are not accurate.

The only thing I’ve found is the Goal Zero Yeti 400 Portable Power Station (or the 500X which uses Li-ion instead of lead acid). The product page actually claims to be able to get 20+ hours out of similar wattage devices.

Would I be fine with a basic APC/CyberPower/etc, lead-acid, 6/8 outlet desktop UPS? Or should I just go with the Goal Zero which specifically claims to do what I need? Or is there another product that might work better/cheaper?

P.S. r/homelab was the most relevant community I could think of, but if there is a better place to ask, please let me know.

🌐
Amazon
amazon.com › 24-hour-battery-backup › s
Amazon.com: 24 Hour Battery Backup
Limited time deal · 2K+ bought in past month · 3K+ bought in past month · 500+ bought in past month · 500+ bought in past month · 8 hour battery backup · battery backup · 24+hour+battery+backup · battery backup power supply · ups battery backup · refrigerator battery backup ·
🌐
Astro Dynetdi
astrodynetdi.com › blog › how-long-does-a-ups-battery-last
UPS Battery Life: Understanding Run Time & Lifetime
In large usage sites, as in hospitals with patient monitoring carts used in thousands, the whole diagnostic system runs off UPS that has been charged overnight and runs all day. Since patient care is a supremely critical mission, such UPS systems on rolling carts must always be in top shape. Innovative UPS systems with intelligent batteries are a massive advantage to the maintenance crew who order, install, and maintain them 24-7-365. They can use software programs to record the health of their UPS systems and maintain a log that helps them procure new batteries or replace the whole UPS system when the time is right before they abruptly hit the end of life.
🌐
Upsbuyer
upsbuyer.com › ups › shop-by-type › extended-runtime-ups.html
Extended Runtime UPS for Long Power Outages | UPSBuyer.com
Extended runtime UPS systems are designed to support mission-critical loads for long periods, whether due to unstable mains power or where generator backup isn’t available. With scalable battery packs, they offer maximum uptime and flexibility.
🌐
Critical Power Supplies
criticalpowersupplies.co.uk › home
UPS & Standby Power - Critical Power Supplies Ltd
March 1, 2021 - Explore Critical Power Supplies range of standby power backup power solutions, including uninterruptible power supplies (UPS) and emergency power systems, power quality solutions. Modular Lithium Ion Solutons.
🌐
Lifewire
lifewire.com › best-uninterrupted-power-supplies-4142625
Keep Your Gadgets Safe With These UPS Battery Backups
December 15, 2025 - The APC BR1500MS2 is a powerful pure sinewave UPS system that delivers cleaner, more stable power for protecting high-end electronics. It combines 10 power outlets with surge protection (six with battery backup) and 900 watts of power to keep ...
🌐
Cppsales
cppsales.com › home › how long can a ups keep equipment running?
How Long Can a UPS Keep Equipment Running? - Computer Power Protection (CPP)
September 22, 2025 - Small desktop UPS systems usually last 5–15 minutes, while larger commercial UPS units with external battery packs can provide backup power for 30 minutes to several hours, ensuring safe shutdown or seamless generator transfer.
🌐
Goldenmate
goldenmateenergy.com › blogs › goldenmate-blog › how-long-will-a-1000va-ups-last
Uninterruptible Power Supply Time: How Many UPS Operation Time Hours? – Goldenmate Battery
September 28, 2024 - Among the most important specs to master is the duration the UPS can last. This guide teaches you how to estimate the uninterruptible power supply hours your system can provide and how to maximize your UPS operation time. Several factors determine how long your battery runs before reaching the cut-off voltage.