There’s a specific process to it. Need a Daikin d checker tool to really further diagnose Answer from loganscanlon7 on reddit.com
🌐
Reddit
reddit.com › r/hvacadvice › daikin mini split- error code u4
r/hvacadvice on Reddit: Daikin Mini split- error code U4
November 25, 2023 -

I’m a little lost on trying to trouble shoot this one, any advice is appreciated. I purchased a 2 ton single head Daikin minisplit system online a few months ago to install in a workshop in my backyard, that I’m in the process of renovating. Everything was going smoothly with the install, doing the majority of the work myself. I am a builder by trade and have done several minisplit installs over the years. I hired an HVAC tech to connect the refrigerant linesets, and evacuate/ pressure test the lines. As far as I can tell the problem came about when I connected the wiring. Unfortunately I crossed the signal line and one of the power lines at the outdoor unit control wiring. When I went to fire up the system, the indoor unit status light started flashing blue, indicating a system error. I realized what had happened then and corrected the wiring. No luck, still flashing blue. Error code retrieval at this point, at the remote control reads U4: communication error. Next I tried pulling the outdoor unit control panel to see if there is a blown fuse. I was able to locate 3 separate fuses but none of them tested bad. Pulled the indoor unit control board and there is one fuse which also checked out ok. Last I try running a separate jumper wire externally to eliminate the possibility that there is an unseen break in the original signal wire. I then try turning the system on again, same thing: indoor unit status light flashing blue and error code U4. Any ideas?

🌐
Reddit
reddit.com › r/hvac › daikin mini split u4 error
r/HVAC on Reddit: Daikin Mini Split U4 Error
August 14, 2025 -

I’ll try to keep this as brief as possible, I’m trying to resolve a U4 code on a single zone RXL09QMVJU, I do not currently have the model handy on the indoor unit. I know the system is old but I’m with one of the few companies in my area that actually repairs things unless a replacement is absolutely necessary.

I’ve been on the phone twice with Daikin tech support, I’ve run through all of the diagnostic procedures they’ve given me so far and even run through others that shouldn’t throw this particular code. At this point both indoor and outdoor boards have been replaced and I’m starting to question if I might have a board that was DOA when I installed it.

Indoor unit turns on, will run on fan mode but any mode that would involve the compressor errors out, I have proper ac voltage to everything, per their procedure Daikin says I should be looking for 53-55v dc at the indoor board from terminal 3 to ground with the communications wire disconnected. I have 75v dc, I also have the sister unit ten feet away in the next room running fine with 75v dc at that indoor board.

Outdoor board sends no voltage to the compressor, fan was ohmed out and fine, emergency cooling runs the indoor unit at full capacity but again outdoor unit doesn’t run at all and I have continuity in the wiring between indoor and outdoor units.

I’ve been getting some inconsistent information from Daikin between the manuals and talking to them so I figured I’d ask here for opinions.

🌐
Reddit
reddit.com › r/hvacadvice › recently installed daikin minisplit unit giving u4 code
r/hvacadvice on Reddit: Recently installed Daikin Minisplit Unit giving U4 code
July 8, 2025 -

I had a Daikin Minisplit System installed in April of this year. About a Month ago the system gave us error code U4 and stopped working. I turned off the breaker turned it back on and it worked fine. I figured a fault must have happened somewhere and that it would be fine. Today the system does the same thing but now if we try resetting it nothing happens.

I called the company that installed it, and they stated it must have been that we used auto mode. They're coming to look tomorrow, but I guess I'm wondering if any other technicians have noticed the same issue? I read the manual after installation and understood all three indoor units needed to be the same mode. It seems odd to me that having it set to auto would cause a failure at this level.

The indoor units are Daikin model FTXV12AVJU9

🌐
Reddit
reddit.com › r/hvacadvice › [daikin vrv] [220 vac] u4-01 error code help
r/hvacadvice on Reddit: [Daikin VRV] [220 VAC] U4-01 Error Code Help
September 6, 2024 -

My air conditioning failed on me some time today when I was at work, and when I returned home it was 92° inside my home. Figures this would happen during the (hopefully) hottest week of the year in Los Angeles. This system was professionally installed in June of 2020, and has worked without issue until now. The company that did it was bought out by another larger firm, and they are unable to send a tech out for another 17 days. I’m kind of SOL there. I change the filters every six months in the air handlers, and regularly hose down/clean the exterior unit. With a basic visual inspection, it does not appear that there are any blockages/impediments to air flow. I have tried powering off both the exterior unit and both interior air handlers by switching off the breakers on two separate occasions. The cooling works for about 10 minutes and then the error message is displayed again on the interior control panel. Any ideas?

🌐
Reddit
reddit.com › r/airconditioners › daikin u4 error sporadically
r/AirConditioners on Reddit: Daikin U4 error sporadically
May 29, 2024 - I have a minisplit Daikin system, and one of the indoor units is giving out U4 error sporadically. Sometimes, it would run for a couple minutes, because it gives out an error, sometimes, it wont turn on at all. The other indoor unit is working fine.
🌐
Reddit
reddit.com › r › hvacadvice › comments › oq4xin › help_diagnose_a_daikin_u4_error
Ayuda a diagnosticar un error U4 de Daikin : r/hvacadvice
July 23, 2021 - My 9k 20 SEER Daikin has started throwing the U4 error after 9 months of perfect operation after install. DIY project so I assume i'm SOL from a warranty standpoint. It's an interesting case because I turn the unit off for about 2 days and it will start working again for 2 to 3 days and then ...
🌐
Reddit
reddit.com › r/hvacadvice › daikin inverter cycling on and off with error code u4
r/hvacadvice on Reddit: Daikin inverter cycling on and off with error code U4
September 26, 2023 - Error code says U4. Is there a way I can fix this myself? I can put in a ticket with management but they are extremely unresponsive. Archived post. New comments cannot be posted and votes cannot be cast. Share ... Daikin multi-split lost nearly 2kg of refrigerant in under three years and engineer is blaming my filter cleaning schedule
🌐
Reddit
reddit.com › r/hvacadvice › u4 fault code
r/hvacadvice on Reddit: U4 Fault Code
August 17, 2024 -

I have a Daikin Minisplit with 3 heads operating off it. It’s been working great and keeping up nice and cool. It cooled off here for a few days, so I decided to turn all 3 heads off. The temps shot back up yesterday and now none of the heads will run on any mode. They all attempt to start but then go to fault mode. The fault I’m getting is U4. I understand that this is a communication/sensing error and most of my research shows that this is a wiring or board issue. The fact that it was working fine, I think I can rule out improper wiring. Any suggestions? Thanks

Find elsewhere
🌐
Reddit
reddit.com › r/airconditioners › can this old daikin be fixed?
r/AirConditioners on Reddit: Can this old Daikin be fixed?
December 2, 2025 -

Living in a house built 1995 with an aircon unit probably just as old. It’s a split system Daikin that was working but now shows an error U4 and will not turn on. A new system is so expensive I wanted to see what’s the likelihood of this being fixed. I’ve tried turning on/off with no luck. Not keen on paying a specialist just to say it all needs replacing. Anyone had this issue & been able to fix it?

🌐
AirReps
airreps.com › 2025 › 11 › understanding-the-u4-error-code-in-daikin-vrv-systems
Understanding the U4 Error Code in Daikin VRV Systems - AirReps
November 19, 2025 - The U4 error code indicates a communication failure between the indoor unit and outdoor unit. Essentially, your system components are having trouble “talking” to each other through the transmission wiring that connects them.
🌐
JustAnswer
justanswer.com › hvac › pphzc-daikins-inverter-giving-u4-error-code.html
Daikin Inverter U4 Error Code? Expert Troubleshooting Guide
August 3, 2024 - The U4 error on a Daikin inverter typically indicates a communication or sensor fault. First, power off the unit for 5 minutes to reset. If persistent, check the indoor unit’s PCB connections and wiring harness for loose or damaged cables.
🌐
JustAnswer
justanswer.com › hvac › bvmqb-u4-error-daikin-indoor-unit-keeps.html
Daikin U4 Error Code: Expert Solutions and Fixes
December 27, 2018 - The U4 error on Daikin units often indicates a fan motor or flap actuator malfunction. First, power off and vacuum dust from the indoor unit’s fan and flap mechanisms. Check for obstructions preventing flap movement.
🌐
Star-supply
star-supply.com › content › Daikin Single- Multi -U4 Error Code.pdf pdf
Daikin Single-Multi U4 Error Codes
U4 Error Codes · Only good for Daikin Single Zones & Multi-Splits-NOT VALID ON VRV OR SKYAIR · *Always refer to the Service Manual for proper procedures* U4 Fault code is a Signal Transmission Error (between Indoor Unit and Outdoor Unit) REQUIRED TOOLS: MEGGER, MULTIMETER WITH MICRO LEADS ·
🌐
ADK Kooling
adk.co.uk › home › air conditioning › daikin error code u4 — vrv communication fault explained
Daikin Error Code U4 | Communication Fault Fix | ADK London
March 23, 2026 - The Daikin controller on the wall is flashing U4. The system won’t respond to any commands — no heating, no cooling, fan won’t start. The facility manager tries powering it off and on from the controller, but U4 comes straight back every time. Staff are asking questions, the building is uncomfortable, and nobody on site knows what U4 means. U4 is one of the most common error codes on Daikin VRV and VRF systems.
Price   $$
Address   Daneshill House, 3 Waterloo Road, UB8 2QX, Uxbridge
🌐
Airway Group
airway-group.co.uk › home › help & advice › daikin air conditioning fault codes explained [infographic]
Daikin Air Conditioning Fault Codes Explained [Infographic] | Airway
April 2, 2026 - U4 – Communication error between indoor and outdoor units/outdoor and BS units – A mistake with the interconnection wires, or an indoor/outdoor PCB fault.
🌐
Silverback Air-con
silverbackaircon.sg › home › aircon error code › daikin error code › ultimate guide to daikin u4 error code
Ultimate Guide to Daikin U4 Error Code - Silverback Air-con
October 28, 2025 - Is your Daikin system displaying the dreaded U4 error code? Learn how to resolve this issue with our ultimate guide to Daikin U4 error code.
🌐
Daikin
my.daikin.eu › content › dam › DASW › supportavdelningen › Felkoder_SM-TS3errorcode_chart.pdf pdf
Simple Self-Diagnosis by Malfunction Code After Sales Service Division (SM-TS3)
“long beep” sound are error code. 8. Press the MODE button to exit from the · diagnosis mode. The display “ ” means the trial operation · mode. 9. Press the ON/OFF button twice to return · to the normal mode. Note: When the remote controller is left untouched · for 60 seconds, it returns to the normal mode. No. 1 · 2 · 3 · 4 · 5 · 6 · 7 · 8 · 9 · 10 · 11 · Code · 00 · U4 ·